5-208 F60 Feeder Protection System GE Multilin
5.6 GROUPED ELEMENTS 5 SETTINGS
5
5.6.9 BREAKER FAILURE (ANSI 50BF/50NBF)
PATH: SETTINGS GROUPED ELEMENTS SETTING GROUP 1(6) BREAKER FAILURE BREAKER FAILURE 1(2)
BREAKER FAILURE 1
BF1 FUNCTION:
Disabled
Range: Disabled, Enabled
MESSAGE
BF1 MODE:
3-Pole
Range: 3-Pole, 1-Pole
MESSAGE
BF1 SOURCE:
SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4
MESSAGE
BF1 USE AMP SUPV:
Yes
Range: Yes, No
MESSAGE
BF1 USE SEAL-IN:
Yes
Range: Yes, No
MESSAGE
BF1 3-POLE INITIATE:
Off
Range: FlexLogic operand
MESSAGE
BF1 BLOCK:
Off
Range: FlexLogic operand
MESSAGE
BF1 PH AMP SUPV
PICKUP: 1.050 pu
Range: 0.001 to 30.000 pu in steps of 0.001
MESSAGE
BF1 N AMP SUPV
PICKUP: 1.050 pu
Range: 0.001 to 30.000 pu in steps of 0.001
MESSAGE
BF1 USE TIMER 1:
Yes
Range: Yes, No
MESSAGE
BF1 TIMER 1 PICKUP
DELAY: 0.000 s
Range: 0.000 to 65.535 s in steps of 0.001
MESSAGE
BF1 USE TIMER 2:
Yes
Range: Yes, No
MESSAGE
BF1 TIMER 2 PICKUP
DELAY: 0.000 s
Range: 0.000 to 65.535 s in steps of 0.001
MESSAGE
BF1 USE TIMER 3:
Yes
Range: Yes, No
MESSAGE
BF1 TIMER 3 PICKUP
DELAY: 0.000 s
Range: 0.000 to 65.535 s in steps of 0.001
MESSAGE
BF1 BKR POS1 φA/3P:
Off
Range: FlexLogic operand
MESSAGE
BF1 BKR POS2 φA/3P:
Off
Range: FlexLogic operand
MESSAGE
BF1 BREAKER TEST ON:
Off
Range: FlexLogic operand
MESSAGE
BF1 PH AMP HISET
PICKUP: 1.050 pu
Range: 0.001 to 30.000 pu in steps of 0.001
MESSAGE
BF1 N AMP HISET
PICKUP: 1.050 pu
Range: 0.001 to 30.000 pu in steps of 0.001
MESSAGE
BF1 PH AMP LOSET
PICKUP: 1.050 pu
Range: 0.001 to 30.000 pu in steps of 0.001