2-24 F60 Feeder Protection System GE Multilin
2.4 SPECIFICATIONS 2 PRODUCT DESCRIPTION
2
FAULT LOCATOR
Method: single-ended
Voltage source: wye-connected VTs, delta-connected
VTs and neutral voltage, delta-connected
VTs and zero-sequence current (approxi-
mation)
Maximum accuracy if: fault resistance is zero or fault currents
from all line terminals are in phase
Relay accuracy: ±1.5% (V > 10 V, I > 0.1 pu)
Worst-case accuracy:
VT
%error
+ user data
CT
%error
+ user data
Z
Line%error
+ user data
METHOD
%error
+ see chapter 8
RELAY ACCURACY
%error
+ (1.5%)
HI-Z
Detections: Arc Suspected, Arc Detected, Downed
Conductor, Phase Identification
PHASOR MEASUREMENT UNIT
Output format: per IEEE C37.118 or IEC 61850-90-5
standard
Number of channels: 14 synchrophasors, 8 analogs, 16 digi-
tals
TVE (total vector error) <1%
Triggering: frequency, voltage, current, power, rate
of change of frequency, user-defined
Reporting rate: 1, 2, 5, 10, 12, 15, 20, 25, 30, 50, or 60
times per second for P and M class, and
100 or 120 times per second for P class
only
Number of clients: One over TCP/IP port and one over
UDP/IP per aggregator
AC ranges: As indicated in appropriate specifications
sections
Network reporting format: 16-bit integer (for IEEE C37.118) or 32-
bit IEEE floating point numbers
Network reporting style: rectangular (real and imaginary for IEEE
C37.188) or polar (magnitude and angle)
coordinates
Post-filtering: none, 3-point, 5-point, 7-point
Calibration: ±5° (angle) and ±5% (magnitude)
2.4.4 METERING
RMS CURRENT: PHASE, NEUTRAL, AND GROUND
Accuracy at
0.1 to 2.0 × CT rating: ±0.25% of reading or ±0.1% of rated
(whichever is greater)
> 2.0 × CT rating: ±1.0% of reading
RMS VOLTAGE
Accuracy: ±0.5% of reading from 10 to 208 V
REAL POWER (WATTS)
Accuracy at 0.1 to 1.5 x
CT rating and 0.8 to
1.2 x VT rating: ±1.0% of reading at –1.0 ≤ PF< –0.8 and
0.8 < PF ≤ 10
REACTIVE POWER (VARS)
Accuracy at 0.1 to 1.5 x
CT rating and 0.8 to
1.2 x VT rating: ±1.0% of reading at –0.2 ≤ PF ≤ 0.2
APPARENT POWER (VA)
Accuracy at 0.1 to 1.5 x
CT rating and 0.8 to
1.2 x VT rating: ±1.0% of reading
WATT-HOURS (POSITIVE AND NEGATIVE)
Accuracy: ±2.0% of reading
Range: ±0 to 1 × 10
6
MWh
Parameters: three-phase only
Update rate: 50 ms
VAR-HOURS (POSITIVE AND NEGATIVE)
Accuracy: ±2.0% of reading
Range: ±0 to 1 × 10
6
Mvarh
Parameters: three-phase only
Update rate: 50 ms
CURRENT HARMONICS
Harmonics: 2nd to 25th harmonic: per phase, dis-
played as a % of f
1
(fundamental fre-
quency phasor)
THD: per phase, displayed as a % of f
1
Accuracy:
HARMONICS: 1. f
1
> 0.4pu: (0.20% + 0.035% / harmonic) of
reading or 0.15% of 100%, whichever is
greater
2. f
1
< 0.4pu: as above plus %error of f
1
THD: 1. f
1
> 0.4pu: (0.25% + 0.035% / harmonic) of
reading or 0.20% of 100%, whichever is
greater
2. f
1
< 0.4pu: as above plus %error of f
1
VOLTAGE HARMONICS
Harmonics: 2nd to 25th harmonic: per phase, dis-
played as a % of f
1
(fundamental fre-
quency phasor)
THD: per phase, displayed as a % of f
1
Accuracy:
HARMONICS: 1. f
1
> 0.4pu: (0.20% + 0.035% / harmonic) of
reading or 0.15% of 100%, whichever is
greater
2. f
1
< 0.4pu: as above plus %error of f
1
THD: 1. f
1
> 0.4pu: (0.25% + 0.035% / harmonic) of
reading or 0.20% of 100%, whichever is
greater
2. f
1
< 0.4pu: as above plus %error of f
1