F-8 F60 Feeder Protection System GE Multilin
F.2 DNP POINT LISTS APPENDIX F
F
F.2DNP POINT LISTS F.2.1 BINARY INPUT POINTS
The DNP binary input data points are configured through the
PRODUCT SETUP  COMMUNICATIONS  DNP / IEC104 POINT
LISTS  BINARY INPUT / MSP POINTS menu. See the Communications section of Chapter 5 for details. When a freeze func-
tion is performed on a binary counter point, the frozen value is available in the corresponding frozen counter point.
BINARY INPUT POINTS
Static (Steady-State) Object Number: 1
Change Event Object Number: 2
Request Function Codes supported: 1 (read), 22 (assign class)
Static Variation reported when variation 0 requested: 2 (Binary Input with status), Configurable
Change Event Variation reported when variation 0 requested: 2 (Binary Input Change with Time), Configurable
Change Event Scan Rate: 8 times per power system cycle
Change Event Buffer Size: 500
Default Class for All Points: 1