5-232 F60 Feeder Protection System GE Multilin
5.7 CONTROL ELEMENTS 5 SETTINGS
5
Figure 5–107: EXAMPLE FLEXLOGIC CONTROL OF A SETTINGS GROUP
5.7.4 SELECTOR SWITCH
PATH: SETTINGS  CONTROL ELEMENTS  SELECTOR SWITCH SELECTOR SWITCH 1(2)
SELECTOR SWITCH 1
SELECTOR 1 FUNCTION:
Disabled
Range: Disabled, Enabled
MESSAGE
SELECTOR 1 FULL
RANGE: 7
Range: 1 to 7 in steps of 1
MESSAGE
SELECTOR 1 TIME-OUT:
5.0 s
Range: 3.0 to 60.0 s in steps of 0.1
MESSAGE
SELECTOR 1 STEP-UP:
Off
Range: FlexLogic operand
MESSAGE
SELECTOR 1 STEP-UP
MODE: Time-out
Range: Time-out, Acknowledge
MESSAGE
SELECTOR 1 ACK:
Off
Range: FlexLogic operand
MESSAGE
SELECTOR 1 3BIT A0:
Off
Range: FlexLogic operand
MESSAGE
SELECTOR 1 3BIT A1:
Off
Range: FlexLogic operand
MESSAGE
SELECTOR 1 3BIT A2:
Off
Range: FlexLogic operand
MESSAGE
SELECTOR 1 3BIT
MODE: Time-out
Range: Time-out, Acknowledge
MESSAGE
SELECTOR 1 3BIT ACK:
Off
Range: FlexLogic operand
MESSAGE
SELECTOR 1 POWER-UP
MODE: Restore
Range: Restore, Synchronize, Sync/Restore
MESSAGE
SELECTOR 1 TARGETS:
Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
SELECTOR 1 EVENTS:
Disabled
Range: Disabled, Enabled
10
1
VIRT IP 1 ON (VI1)
2
CONT IP 1 ON (H5A)
3
OR (2)
OR (2)
4
PHASE TOC1 PKP
5
NOT
6
PHASE TOC2 PKP
7
NOT
8
AND (3)
AND (3)
9
=VIRTOP1(VO1)
=VIRTOP1(VO1)
END