GE Multilin F60 Feeder Protection System 6-25
6 ACTUAL VALUES 6.3 METERING
6
6.3.8 IEC 61580 GOOSE ANALOG VALUES
PATH: ACTUAL VALUES METERING IEC 61850 GOOSE ANALOGS
The F60 Feeder Protection System is provided with optional IEC 61850 communications capability. This
feature is specified as a software option at the time of ordering. See the Order Codes section of chapter 2
for details.
The IEC 61850 GGIO3 analog input data points are displayed in this menu. The GGIO3 analog data values are received
via IEC 61850 GOOSE messages sent from other devices.
6.3.9 WATTMETRIC GROUND FAULT
PATH: ACTUAL VALUES METERING WATTMETRIC GROUND FAULT 1(2)
This menu displays the wattmetric zero-sequence directional element operating power values.
6.3.10 PHASOR MEASUREMENT UNIT
PATH: ACTUAL VALUES METERING PHASOR MEASUREMENT UNIT PMU 1
SOURCE VOLTAGE V
BASE
= maximum nominal primary RMS value of the +IN and –IN inputs
SYNCHROCHECK
(Max Delta Volts)
V
BASE
= maximum primary RMS value of all the sources related to the +IN and –IN inputs
IEC 61850
GOOSE ANALOGS
ANALOG INPUT 1
0.000
MESSAGE
ANALOG INPUT 2
0.000
MESSAGE
ANALOG INPUT 3
0.000
↓
MESSAGE
ANALOG INPUT 32
0.000
WATTMETRIC
GROUND FAULT 1
WATT GND FLT 1:
0.000 W
PMU 1
PMU 1 VA:
0.0000 kV, 0.00°
Range: Va or Vab per VT bank connection
MESSAGE
PMU 1 VB:
0.0000 kV, 0.00°
Range: Va or Vab per VT bank connection
MESSAGE
PMU 1 VC:
0.0000 kV, 0.00°
Range: Va or Vab per VT bank connection
MESSAGE
PMU 1 VX:
0.0000 kV, 0.00°
MESSAGE
PMU 1 V1:
0.0000 kV, 0.00°
Table 6–2: FLEXELEMENT BASE UNITS (Sheet 2 of 2)