GE Multilin F60 Feeder Protection System 7-7
7 COMMANDS AND TARGETS 7.1 COMMANDS
7
•A RELAY OUT OF SERVICE event is recorded.
b) MAJOR SELF-TEST ERROR MESSAGES
The major self-test errors are outlined in this section.
Latched target message: Yes.
Description of problem: One or more installed hardware modules is not compatible with the F60 order code.
How often the test is performed: Module dependent.
What to do: Contact the factory and supply the failure code noted in the display. The “xxx” text identifies the failed mod-
ule (for example, F8L).
Latched target message: No.
Description of problem: The configuration of modules does not match the order code stored in the F60.
How often the test is performed: On power up. Afterwards, the backplane is checked for missing cards every five sec-
onds.
What to do: Check all modules against the order code, ensure they are inserted properly, and cycle control power. If
the problem persists, contact the factory.
Latched target message: No.
Description of problem: A FlexLogic equation is incorrect.
How often the test is performed: The test is event driven, performed whenever FlexLogic equations are modified
.
What to do: Finish all equation editing and use self tests to debug any errors.
Latched target message: No.
Description of problem: The
PRODUCT SETUP  INSTALLATION RELAY SETTINGS setting indicates the F60 is not pro-
grammed.
How often the test is performed: On power up and whenever the
PRODUCT SETUP  INSTALLATION RELAY SETTINGS
setting is altered.
What to do: Program all settings and then set PRODUCT SETUP  INSTALLATION RELAY SETTINGS to “Programmed”
Latched target message: Yes.
Description of problem: Module hardware failure detected. Module Failures 1 to 11 are major. The system can reboot
for four of these, as follows.
MODULE FAILURE 06 — Event message reads SYSTEM INTEGRITRY RECOVERY 06 when a reboot was required
and otherwise MODULE FAILURE 06 when a failure was detected
INCOMPATIBLE H/W:
Contact Factory (xxx)
EQUIPMENT MISMATCH:
with 2nd line detail
FLEXLOGIC ERROR:
with 2nd line detail
UNIT NOT PROGRAMMED:
Check Settings
MODULE FAILURE___:
Contact Factory (xxx)