B-78 F60 Feeder Protection System GE Multilin
B.4 MEMORY MAPPING APPENDIX B
B
Phasor Measurement Unit df/dt Trigger (Read/Write Setting)
EB3A PMU 1 df/dt Trigger Function 0 to 1 --- 1 F102 0 (Disabled)
EB3B PMU 1 df/dt Trigger Raise 0.1 to 15 Hz/s 0.01 F001 25
EB3C PMU 1 df/dt Trigger Fall 0.1 to 15 Hz/s 0.01 F001 25
EB3D PMU 1 df/dt Trigger Pkp Time 0 to 600 s 0.01 F001 10
EB3E PMU 1 df/dt Trigger Dpo Time 0 to 600 s 0.01 F001 100
EB3F PMU 1 df/dt Trigger Block (3 items) 0 to 4294967295 --- 1 F300 0
EB45 PMU 1 df/dt Trigger Target 0 to 2 --- 1 F109 0 (Self-reset)
EB46 PMU 1 df/dt Trigger Events 0 to 1 --- 1 F102 0 (Disabled)
Phasor Measurement Unit Power Trigger (Read/Write Setting)
EB88 PMU 1 Power Trigger Function 0 to 1 --- 1 F102 0 (Disabled)
EB89 PMU 1 Power Trigger Active 0.25 to 3 pu 0.001 F001 1250
EB8A PMU 1 Power Trigger Reactive 0.25 to 3 pu 0.001 F001 1250
EB8B PMU 1 Power Trigger Apparent 0.25 to 3 pu 0.001 F001 1250
EB8C PMU 1 Power Trigger Pkp Time 0 to 600 s 0.01 F001 10
EB8D PMU 1 Power Trigger Dpo Time 0 to 600 s 0.01 F001 100
EB8E PMU 1 Power Trigger Block (3 items) 0 to 4294967295 --- 1 F300 0
EB94 PMU 1 Power Trigger Target 0 to 2 --- 1 F109 0 (Self-reset)
EB95 PMU 1 Power Trigger Events 0 to 1 --- 1 F102 0 (Disabled)
Phasor Measurement Unit Calibration (Read/Write Setting)
EBDC PMU 1 Va Calibration Angle -5 to 5 ° 0.05 F002 0
EBDD PMU 1 Va Calibration Magnitude 95 to 105 % 0.1 F002 1000
EBDE PMU 1 Vb Calibration Angle -5 to 5 ° 0.05 F002 0
EBDF PMU 1 Vb Calibration Magnitude 95 to 105 % 0.1 F002 1000
EBE0 PMU 1 Vc Calibration Angle -5 to 5 ° 0.05 F002 0
EBE1 PMU 1 Vc Calibration Magnitude 95 to 105 % 0.1 F002 1000
EBE2 PMU 1 Vx Calibration Angle -5 to 5 ° 0.05 F002 0
EBE3 PMU 1 Vx Calibration Magnitude 95 to 105 % 0.1 F002 1000
EBE4 PMU 1 Ia Calibration Angle -5 to 5 ° 0.05 F002 0
EBE5 PMU 1 Ia Calibration Magnitude 95 to 105 % 0.1 F002 1000
EBE6 PMU 1 Ib Calibration Angle -5 to 5 ° 0.05 F002 0
EBE7 PMU 1 Ib Calibration Magnitude 95 to 105 % 0.1 F002 1000
EBE8 PMU 1 Ic Calibration Angle -5 to 5 ° 0.05 F002 0
EBE9 PMU 1 Ic Calibration Magnitude 95 to 105 % 0.1 F002 1000
EBEA PMU 1 Ig Calibration Angle -5 to 5 ° 0.05 F002 0
EBEB PMU 1 Ig Calibration Magnitude 95 to 105 % 0.1 F002 1000
EBEC PMU 1 Sequence Voltage Shift Angle -180 to 180 ° 30 F002 0
EBED PMU 1 Sequence Current Shift Angle -180 to 180 ° 30 F002 0
Phasor Measurement Unit Network Reporting Configuration (Read/Write Setting)
EC48 PMU Network Reporting Function 0 to 1 --- 1 F102 0 (Disabled)
EC49 PMU Network Reporting ID Code 1 to 65534 --- 1 F001 1
EC4A PMU TCP Port Number 1 to 65535 --- 1 F001 4712
EC4B PMU UDP Port Number 1 1 to 65535 --- 1 F001 4713
EC4C PMU UDP Port Number 2 1 to 65535 --- 1 F001 4714
Settings File Template (Read/Write Setting)
ED00 FlexLogic Displays Active 0 to 1 --- 1 F102 1 (Enabled)
ED01 Template Access --- --- --- F205 (none)
Setting File Template (Read Only Non-Volatile)
ED07 Last Settings Change Date 0 to 4294967295 --- 1 F050 0
Settings File Template (Read/Write Setting)
ED09 Template Bitmask (750 items) 0 to 65535 --- 1 F001 0
Phasor Measurement Unit Records (Read Only)
EFFF PMU Recording Number of Triggers 0 to 65535 --- 1 F001 0
Table B–10: MODBUS MEMORY MAP (Sheet 70 of 70)
ADDR REGISTER NAME RANGE UNITS STEP FORMAT DEFAULT