4
Inverter and peripheral devices
1.2.1 Peripheral devices
Check the motor capacity of the inverter you purchased. Appropriate peripheral devices must be selected according
to the capacity. Refer to the following list and prepare appropriate peripheral devices:
200V class
Motor
Output (kW)
*1
Applicable Inverter Type
Breaker Selection*2,4
Input Side Magnetic
Contactor*3
Reactor connection
with commercial
power-supply
operation
Reactor connection
without with
without
with
0.75 FR-F720-0.75K 30AF 10A 30AF 10A 30AF 10A S-N10 S-N10
1.5 FR-F720-1.5K 30AF 15A 30AF 15A 30AF 15A S-N10 S-N10
2.2 FR-F720-2.2K 30AF 20A 30AF 15A 30AF 20A S-N10 S-N10
3.7 FR-F720-3.7K 30AF 30A 30AF 30A 30AF 30A S-N20, N21 S-N10
5.5 FR-F720-5.5K 50AF 50A 50AF 40A 50AF 50A S-N25 S-N20, N21
7.5 FR-F720-7.5K 100AF 60A 50AF 50A 100AF 60A S-N25 S-N25
11 FR-F720-11K 100AF 75A 100AF 75A 100AF 75A S-N35 S-N35
15 FR-F720-15K 225AF 125A 100AF 100A 225AF 125A S-N50 S-N50
18.5 FR-F720-18.5K 225AF 150A 225AF 125A 225AF 150A S-N65 S-N50
22 FR-F720-22K 225AF 175A 225AF 150A 225AF 175A S-N80 S-N65
30 FR-F720-30K 225AF 225A 225AF 175A 225AF 225A S-N95 S-N80
37 FR-F720-37K 400AF 250A 225AF 225A 400AF 250A S-N150 S-N125
45 FR-F720-45K 400AF 300A 400AF 300A 400AF 350A S-N180 S-N150
55 FR-F720-55K 400AF 400A 400AF 350A 600AF 500A S-N220 S-N180
75 FR-F720-75K  400AF 400A 400AF 400A 
S-N300
90 FR-F720-90K  400AF 400A 600AF 500A 
S-N300
110 FR-F720-110K  600AF 500A 600AF 600A 
S-N400
*1 Selections for use of the Mitsubishi 4-pole standard motor with power supply voltage of 200VAC 50Hz.
*2 Select the MCCB according to the inverter power supply capacity.
Install one MCCB per inverter.
For installations in the United States or Canada, use the fuse certified by the UL and cUL.
(Refer to the Instruction Manual (basics).)
*3 Magnetic contactor is selected based on the AC-1 class. The electrical durability of magnetic contactor is 500,000 times. When the magnetic
contactor is used for emergency stop during motor driving, the electrical durability is 25 times.
When using the MC for emergency stop during motor driving or using on the motor side during commercial-power supply operation, select the
MC with class AC-3 rated current for the motor rated current.
*4 When the breaker on the inverter primary side trips, check for the wiring fault (short circuit), damage to internal parts of the inverter, etc.
Identify the cause of the trip, then remove the cause and power on the breaker.
MCCB INV
MCCB INV
IM
IM