158
Selection of operation mode and
operation location
4.18 Selection of operation mode and operation location
4.18.1 Operation mode selection (Pr. 79)
The above parameters can be changed during a stop in any operation mode.
Purpose Parameter that must be set Refer to page
Operation mode selection Operation mode selection Pr. 79 158
Started in network operation mode Operation mode at power on Pr. 79, Pr. 340 166
Selection of control location
Sslection of control source, speed
command source and control location
during communication operation
Pr. 338, Pr. 339,
Pr. 550, Pr. 551
167
Used to select the operation mode of the inverter.
Mode can be changed as desired between operation using external signals (external operation), operation from
the PU (FR-DU07/FR-PU04/FR-PU07), combined operation of PU operation and external operation (external/PU
combined operation, and network operation (when RS-485 terminals or a communication option is used).
Parameter
Number
Name
Initial
Value
Setting
Range
Description
LED Indication
: Off
: On
79
Operation
mode
selection
0
0
Use external/PU switchover mode (press to switch
between the PU and external operation mode.
At power on, the inverter is placed in the external
operation mode.
External operation mode
PU operation mode
1 Fixed to PU operation mode
2
Fixed to external operation mode
Operation can be performed by switching between the
external and Net operation mode.
External operation mode
NET operation mode
3
External/PU combined operation mode 1
Running frequency Start signal
PU (FR-DU07/FR-PU04/FR-
PU07) setting or external signal
input (multi-speed setting,
across terminals 4-5 (valid
when AU signal turns on)).
External signal input
(terminal STF, STR)
4
External/PU combined operation mode 2
Running frequency Start signal
External signal input
(Terminal 2, 4, 1, JOG, multi-
speed selection, etc.)
Input from the PU (FR-
DU07/FR-PU04/FR-
PU07)
(, )
6
Switch-over mode
Switch among PU operation, external operation, and NET
operation while keeping the same operating status.
PU operation mode
External operation mode
NET operation mode
7
External operation mode (PU operation interlock)
X12 signal ON*
Operation mode can be switched to the PU operation
mode.
(output stop during external operation)
X12 signal OFF*
Operation mode can not be switched to the PU
operation mode.
PU operation mode
External operation mode