114
Function assignment of external
terminal and control
4.10.8 Remote output function (REM signal, Pr. 495 to Pr. 497)
You can utilize the on/off of the inverter's output signals instead of the remote output terminal of the
programmable logic controller.
Parameter
Number
Name Initial Value Setting Range Description
495 Remote output selection 0
0
Remote output data clear at powering
off
1
Remote output data held at powering
off
496 * Remote output data 1 0 0 to 4095
Refer to the following diagram.
497 * Remote output data 2 0 0 to 4095
The above parameters can be set when Pr. 160 User group read selection = "0". (Refer to page 156)
* The above parameters allow its setting to be changed during operation in any operation mode even if "0" (initial value) is set in
Pr. 77 Parameter write selection.
<Remote output data>
Pr. 496
Pr. 497
*1 As desired
*2 Y0 to Y6 are available only when the extension output option (FR-
A7AY) is fitted
*3 RA1 to RA3 are available only when the relay output option (FR-A7AR)
is fitted
â‹… The output terminal can be turned on/off depending
on the Pr. 496 or Pr. 497 setting. The remote output
selection can be controlled on/off by computer link
communication from the PU connector or RS-485
port or by communication from the communication
option.
â‹… Set "96" (positive logic) or "196" (negative logic) to
any of Pr. 190 to Pr. 196 (output terminal function
selection), and assign the remote output (REM)
signal to the terminal used for remote output,
â‹… When you refer to the left diagram and set 1 to the
terminal bit (terminal where the REM signal has
been assigned) of Pr. 496 or Pr. 497, the output
terminal turns on (off for negative logic). By setting
0, the output terminal turns off (on for negative
logic).
Example)When "96" (positive logic) is set to Pr. 190 RUN terminal function selection and "1" (H01) is set to Pr. 496,
the terminal RUN turns on.
ON/OFF example for positive logic
â‹… When Pr. 495 = "0" (initial value), performing a power
supply reset (including a power failure) clears the REM
signal output. (The ON/OFF states of the terminals are
as set in Pr. 190 to Pr. 196.) The Pr. 496 and Pr. 497
settings are also "0".
When Pr. 495 = "1", the remote output data before power
supply-off is stored into the EEPROM, so the signal
output at power recovery is the same as before power
supply-off. However, it is not stored when the inverter is
reset (terminal reset, reset request through
communication).
(See the chart on the left)
REMARKS
â‹… The output terminal where the REM signal is not assigned using any of Pr. 190 to Pr. 196 does not turn on/off if 0/1 is set to the
terminal bit of Pr. 496 or Pr. 497 . (It turns on/off with the assigned function.)
â‹… When the inverter is reset (terminal reset, reset request through communication), Pr. 496 and Pr. 497 values turn to "0". When Pr.
495 = "1", however, they are the settings at power supply-off. (The settings are stored at power supply-off.)
CAUTION
â‹… When Pr. 495 = "1"(remote output data retention even at powering off), take such a step as to connect R1/L11, S1/L21 and P/+,
N/- to ensure that control power will be retained to some degree. If you do not take such a step, the output signals provided after
power-on are not guaranteed.
♦ Parameters referred to ♦
â‹… Pr. 190 to Pr. 196 (output terminal function selection) Refer to page 107
b11 b0
ABC1
ABC2
*1
*1
*1
*1
*1
FU
OL
IPF
SU
RUN
b11 b0
Y5 *2
Y6 *2
RA1 *3
RA2 *3
RA3 *3
*1
*1
Y4 *2
Y3 *2
Y2 *2
Y1 *2
Y0 *2
Power
supply
Power
supply
OFF OFF
ONOFF
REMREM
REM signal clear REM signal held
Inverter
reset time
(about 1s)
Pr.495 = 0
Pr.495 = 1

Table of Contents

Questions and Answers:

Mitsubishi Electric F700 Specifications

General IconGeneral
BrandMitsubishi Electric
ModelF700
CategoryInverter
LanguageEnglish

Summary

OUTLINE

Product checking and parts identification

Instructions for unpacking and verifying the inverter and its capacity plate.

Inverter and peripheral devices

Details on the inverter and associated peripheral devices like power supply and PLC.

Method of removal and reinstallation of the front cover

Step-by-step guide for removing and reinstalling the inverter's front cover.

Installation of the inverter and enclosure design

Considerations for designing and manufacturing inverter enclosures, including environmental factors.

WIRING

Terminal connection diagram

Diagram illustrating the terminal connections for the main and control circuits.

EMC filter

Explanation of the built-in EMC filter and its ON/OFF settings.

Main circuit terminal specifications

Specifications for the main circuit terminals, including AC power input and inverter output.

Cables and wiring length

Recommendations for cable size and wiring length to ensure proper voltage drop and torque.

PRECAUTIONS FOR USE OF THE INVERTER

Noise and leakage currents

Discussion on noise and leakage currents, their causes, and countermeasures.

Power supply harmonics

Explanation of power supply harmonics generated by the inverter and suppression techniques.

Harmonic suppression guideline

Guidelines for harmonic suppression to protect consumers from outgoing harmonic currents.

Installation of a reactor

Guidance on installing AC or DC reactors to prevent excessive peak current.

Inverter-driven 400V class motor

Measures to address surge voltage issues when driving 400V class motors.

Precautions for use of the inverter

General precautions for handling and operating the inverter to prevent damage or shortened lifespan.

PARAMETERS

Operation panel (FR-DU07)

Description of the parts and basic operation of the FR-DU07 operation panel.

Parameter List

Comprehensive list of inverter parameters with their names, ranges, and descriptions.

Adjust the output torque of the motor (current)

Methods to adjust motor output torque, including manual torque boost and magnetic flux vector control.

Limit the output frequency

Procedures for setting maximum/minimum output frequencies and avoiding mechanical resonance points.

Set V/F pattern

Guidelines for setting V/F patterns, including base frequency, voltage, and load patterns.

Frequency setting by external terminals

How to set frequency using external terminals, including multi-speed and jog operations.

Setting of acceleration/deceleration time and acceleration/deceleration pattern

Configuration of acceleration/deceleration times and patterns, including starting frequency.

Selection and protection of a motor

Details on motor protection features like thermal relay and applied motor settings.

Motor brake and stop operation

Methods for motor braking and stopping, including DC injection brake and regenerative brake.

Function assignment of external terminal and control

Mapping input/output terminals to various functions and control logic.

Monitor display and monitor output signal

How to configure and use monitor displays and output signals for various parameters.

Misoperation prevention and parameter setting restriction

Settings to prevent misoperation, including parameter write protection and PU disconnection.

Energy saving operation and energy saving monitor

Features for energy saving control and monitoring of power consumption.

Motor noise, noise reduction

Techniques to reduce motor noise by adjusting PWM carrier frequency and Soft-PWM control.

Frequency setting by analog input (terminal 1, 2, 4)

Configuration of analog inputs for frequency setting and compensation.

Misoperation prevention and parameter setting restriction

Settings to prevent misoperation, including parameter write protection and PU disconnection.

Selection of operation mode and operation location

Guidelines for selecting operation modes and controlling the inverter via terminals or communication.

PROTECTIVE FUNCTIONS

Reset method of protective function

Procedure for resetting protective functions and handling alarms and warnings.

List of alarm display

Table listing operation panel indications for errors, warnings, and major faults with referenc

Causes and corrective actions

Troubleshooting guide for common error messages, including descriptions and corrective actions.

PRECAUTIONS FOR MAINTENANCE AND INSPECTION

Inspection item

General inspection items to prevent faults, including daily checks.

Daily and periodic inspection

Detailed inspection checklist for various components and environmental conditions.

Display of the life of the inverter parts

How to check the estimated life of inverter components like capacitors and cooling fans.

Checking the inverter and converter modules

Procedure for checking inverter and converter modules using a tester.

Cleaning

Guidelines for cleaning the inverter unit to maintain its performance.

Replacement of parts

Information on periodically replacing parts like cooling fans and capacitors.

SPECIFICATIONS

Rating

Detailed rating specifications for 200V and 400V class inverters, including capacity and current.

Common specifications

General specifications covering control methods, frequency accuracy, and protective functions.

Outline dimension drawings

Physical dimensions and mounting hole details for various inverter models.

Heatsink protrusion attachment procedure

Instructions for installing the inverter with heatsink protrusion for improved heat dissipation.

Related product manuals