Page #262 background image
254
Inspection item
6.1.4 Display of the life of the inverter parts
The self-diagnostic alarm is output when the life span of the control circuit capacitor, cooling fan, each parts of the
inrush current limit circuit is near to give an indication of replacement time .
The life alarm output can be used as a guideline for life judgement.
Refer to page 217 to perform the life check of the inverter parts.
6.1.5 Checking the inverter and converter modules
<Preparation>
(1) Disconnect the external power supply cables (R/L1, S/L2, T/L3) and motor cables (U, V, W).
(2) Prepare a tester. (Use 100Ω range.)
<Checking method>
Change the polarity of the tester alternately at the inverter terminals R/L1, S/L2, T/L3, U, V, W, P/+ and N/−, and check
for continuity.
<Module device numbers and terminals to be checked>
(Assumes the use of an analog meter.)
Parts Judgement level
Main circuit capacitor 85% of the initial capacity
Control circuit capacitor Estimated 10% life remaining
Inrush current limit circuit Estimated 10% life remaining (Power on: 100,000 times left)
Cooling fan Less than 50% of the predetermined speed
CAUTION
1. Before measurement, check that the smoothing capacitor is discharged.
2. At the time of discontinuity, due to the smothing capacitor, the tester may not indicate ∞. At the time of continuity, the
measured value is several to several ten's-of ohms depending on the module type, circuit tester type, etc. If all measured
values are almost the same, the modules are without fault.
Tester Polarity
Measured
Value
Tester Polarity
Measured
Value
Converter
module
D1
R/L1 P/+ Discontinuity
D4
R/L1 N/− Continuity
P/+ R/L1 Continuity N/− R/L1 Discontinuity
D2
S/L2 P/+ Discontinuity
D5
S/L2 N/− Continuity
P/+ S/L2 Continuity N/− S/L2 Discontinuity
D3
T/L3 P/+ Discontinuity
D6
T/L3 N/− Continuity
P/+ T/L3 Continuity N/− T/L3 Discontinuity
Inverter
module
TR1
UP/+ Discontinuity
TR4
UN/− Continuity
P/+ U Continuity N/− U Discontinuity
TR3
VP/+ Discontinuity
TR6
VN/− Continuity
P/+ V Continuity N/− V Discontinuity
TR5
WP/+ Discontinuity
TR2
WN/− Continuity
P/+ W Continuity N/− W Discontinuity
Converter module Inverter module
D1 D2 D3
D4 D5 D6
TR1 TR3 TR5
TR4 TR6 TR2
U
V
W
R/L1
S/L2
T/L3
C
P/+
N/−

Table of Contents