134
Operation setting at alarm occurrence
4.13.2 Alarm code output selection (Pr.76)
â‹… By setting Pr. 76 to "1" or "2", the alarm code can be output to the output terminals.
â‹… When the setting is "2", an alarm code is output at only alarm occurrence, and during normal operation, the terminals
output the signals assigned to Pr. 190 to Pr. 196 (output terminal function selection).
â‹… The following table indicates alarm codes to be output. (0: output transistor off, 1: output transistor on)
At alarm occurrence, its description can be output as a 4-bit digital signal from the open collector output
terminals.The alarm code can be read by a programmable controller, etc., and its corrective action can be shown
on a display, etc.
Parameter
Number
Name Initial Value Setting Range Description
76 Alarm code output selection 0
0 Without alarm code output
1
With alarm code output
(Refer to the following table)
2
Alarm code output at alarm occurrence
only (Refer to the following table)
The above parameters can be set when Pr. 160 User group read selection = "0". (Refer to page 156)
Operation Panel
Indication
(FR-DU07)
Output of Output Terminals
Alarm Code
SU IPF OL FU
Normal * 0000 0
E.OC1 0001 1
E.OC2 0010 2
E.OC3 0011 3
E.OV1 to E.OV3 0100 4
E.THM 0101 5
E.THT 0110 6
E.IPF 0111 7
E.UVT 1000 8
E.FIN 1001 9
E. BE 1010 A
E. GF 1011 B
E.OHT 1100 C
E.OLT 1101 D
E.OPT 1110 E
E.OP1 1110 E
Other than the above 1111 F
* When Pr. 76 = "2", the output terminals output the signals assigned to Pr. 190 to Pr. 196 .
CAUTION
â‹… When a value other than "0" is set in Pr.76
When an alarm occurs, the output terminals SU, IPF, OL, FU output the signal in the above table, independently of the Pr. 190 to
Pr. 196 (output terminal function selection) settings. Please be careful when inverter control setting has been made with the outut
signals of Pr. 190 to Pr. 196.
♦ Parameters referred to ♦
Pr. 190 to Pr. 196 (output terminal function selection) Refer to page 107