EasyManuals Logo
Home>GE>Controller>F650

GE F650 User Manual

GE F650
801 pages
To Next Page IconTo Next Page
To Next Page IconTo Next Page
To Previous Page IconTo Previous Page
To Previous Page IconTo Previous Page
Page #346 background imageLoading...
Page #346 background image
GEK-106310AB F650 Digital Bay Controller 6-23
6 ACTUAL VALUES 6.2 STATUS
6
SWITCH X 11_ERROR Output that represents the Switchgear status 11, considered as abnormal.
SWITCH X OPEN INIT Programmable input that indicates the initiation of the Opening Operation for the considered
switchgear.
SWITCH X CLOSE INIT Programmable input that indicates the initiation of the closing Operation for the considered
switchgear.
SWGR X FAIL TO OPEN Output that represents a failure to open, from the associated external device (opening time
exceeded)
SWGR X FAIL TO CLOSE Output that represents a failure to close from the associated external device (closing time
exceeded)
See attached figure
Figure 6–1: SWITCHGEAR CONTACTS
6.2.9 CALIBRATION
This screen can be accessed at Actual> Status > Calibration, and it includes the internal calibration status for the relay.
Table 6–28: CALIBRATION STATUS
FACTORY CALIBRATION: This value will be active when the relay calibration settings are the default values (no
calibration).
CALIBRATION ERROR: Error shown when there is a problem in the calibration settings (wrong values).
CALIBRATION
FACTORY CALIBRATION
CALIBRATION ERROR
SWGR X FAIL TO OPEN
SWGR X FAIL TO CLOSE
SWITCH X OPEN
INIT
SWITCH X CLOSE
INIT
SWITCH X B
INPUT
SWITCH X A STATUS
SWITCH X A
INPUT
SWITCH X B STATUS
SWITCH X OPEN
SWITCH X
CLOSED
SWITCH X
00
_
ERROR
SWITCH X
11
_
ERROR
Switchgear logic
module

Table of Contents

Other manuals for GE F650

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F650 and is the answer not in the manual?

GE F650 Specifications

General IconGeneral
BrandGE
ModelF650
CategoryController
LanguageEnglish

Related product manuals