GEK-106310AB F650 Digital Bay Controller 6-23
6 ACTUAL VALUES 6.2 STATUS
6
SWITCH X 11_ERROR Output that represents the Switchgear status 11, considered as abnormal.
SWITCH X OPEN INIT Programmable input that indicates the initiation of the Opening Operation for the considered
switchgear.
SWITCH X CLOSE INIT Programmable input that indicates the initiation of the closing Operation for the considered
switchgear.
SWGR X FAIL TO OPEN Output that represents a failure to open, from the associated external device (opening time
exceeded)
SWGR X FAIL TO CLOSE Output that represents a failure to close from the associated external device (closing time
exceeded)
See attached figure
Figure 6–1: SWITCHGEAR CONTACTS
6.2.9 CALIBRATION
This screen can be accessed at Actual> Status > Calibration, and it includes the internal calibration status for the relay.
Table 6–28: CALIBRATION STATUS
FACTORY CALIBRATION: This value will be active when the relay calibration settings are the default values (no
calibration).
CALIBRATION ERROR: Error shown when there is a problem in the calibration settings (wrong values).
CALIBRATION
FACTORY CALIBRATION
CALIBRATION ERROR
SWGR X FAIL TO OPEN
SWGR X FAIL TO CLOSE
SWITCH X OPEN
INIT
SWITCH X CLOSE
INIT
SWITCH X B
INPUT
SWITCH X A STATUS
SWITCH X A
INPUT
SWITCH X B STATUS
SWITCH X OPEN
SWITCH X
CLOSED
SWITCH X
00
ERROR
Switchgear logic
module