C-10 F650 Digital Bay Controller GEK-106310AB
C.4 BINARY INPUT POINTS APPENDIX C
C
C.4BINARY INPUT POINTS
The F650 relay has a configurable Map of DNP Binary Input points. This map can be formed by up to 10 blocks of 16 binary
states that are configured using “Setpoint->Relay Configuration” menu from the EnerVista 650 Setup program. The
minimum number of DNP Binary Input points is 16 and the maximum number is 160. Within these 160 DNP points, 128 bits
(8 blocks of 16) are mapped to Control Events ("Setpoint->Relay Configuration->Control Events") and 32 bits (2 block
of 16) are mapped to contacts A, B of 16 Switchgears ("Setpoint->Relay Configuration->Switchgear"). Each Switchgear
in F650 is mapped into two DNP Binary Input points. Lets say the setting Binary Input Block1 has been set the value
Switchgear 1-8, it means that DNP Binary Input point 0 = Switchgear 1Contact A, DNP Binary Input point 1 = Switchgear 1
Contact B, DNP Binary Input point 2 = Switchgear 2 Contact A, etc.
To each Control Event or Switchgear Contact, the user can assign any of the binary states of the F650 relay. These states
are contact inputs and outputs, virtual outputs, protection element states, PLC states, etc. DNP Points that correspond to
Control Events o Switchgear Contacts that are not configured will have a zero value in the response.
Using the PLC-Editor, through the EnerVista 650 Setup program, selecting menu: "Setpoint->Logic Configuration", it will
be possible to implement complex logic, more than simple OR and NOT previous functions. To perform this, in the menu:
"Setpoint->Relay Configuration->Control Events" assign a Virtual Output to selected point, after that, implement wished
logic with the PLC-Editor.
DEFAULT BINARY INPUT POINTS MAP
BINARY INPUT POINTS
Static (Steady-State) Object Number: 1
Change Event Object Number: 2
Request Function Codes supported: 1 (read), 22 (assign class)
Static Variation Reported when variation 0 requested: 2 (Binary Input Change with status)
Change Event Variation reported when variation 0 requested: 2 (Binary Input Change with Time)
Default Class for all points: 1
POINT
INDEX
NAME/DESCRIPTION
0-127 Control Events 1-128
128 Switchgear 1 Contact A
129 Switchgear 1 Contact B
130 Switchgear 2 Contact A
131 Switchgear 2 Contact B
132 Switchgear 3 Contact A
133 Switchgear 3 Contact B
134 Switchgear 4 Contact A
135 Switchgear 4 Contact B
136 Switchgear 5 Contact A
137 Switchgear 5 Contact B
138 Switchgear 6 Contact A
139 Switchgear 6 Contact B
140 Switchgear 7 Contact A
141 Switchgear 7 Contact B
142 Switchgear 8 Contact A

Table of Contents