2-26 F650 Digital Bay Controller GEK-106310AB
2.4 TECHNICAL SPECIFICATIONS 2 PRODUCT DESCRIPTION
2
2.4.6.6 IRIG-B INPUT
2.4.7 REAL TIME CLOCK
Note: When the relay's date and time is changed using any of the documented methods (Modbus, Irig-b, Sntp, Front
Panel…) the relay acknowledges and updates the time instantly but it is not until after nearly 3 minutes that it is
permanently stored in the Real Time Clock’s NVRAM.
2.4.8 OUTPUTS
2.4.8.1 REMOTE OUTPUTS (IEC61850 GSSE/GOOSE)
Amplitude modulation: DC SHIFT = Demodulated input (no carrier)
Input Voltage: TTL
Input Burden: 1.5 mA
Input Impedance: 3.3 kOhm
Minimum Input Voltage: 2.4 V
Maximum Input Voltage:
± 24 V
Formats: B000 (*) B001, B002 and B003 (*)
(*) Signal combinations recognized in accordance with IRIG Standard 200-95
Isolation: 2 kV
Accuracy:
Typical ±20 ppm
Backup energy: More than 1 week
Single Contact Carry continuous: 16 A
Make and Carry for 1 sec. 60 A
Break at L/R of 40 ms: 0.3 A DC max. at 125 Vdc
0.25 A DC max. at 250 Vdc
Operate Time: < 8 ms
Contact material: Silver Alloy
Output Logic Type, Output Type and Pulse Output Time are selectable by setting for each output
Output Logic Type Positive / Negative
Output Type Normal / Pulse / Latch (Selectable by setting for each output)
Pulse Output Time 0 to 60000 ms in steps of 1 ms (applicable only to signals set as pulse type)
Separate operate and reset signal can be configured by any digital signal programmable through PLC
Contact Outputs (F31-F33, F34-F36) for
board type 2 (supervision) in slot F:
The current seal-in circuit is used for verifying the current condition in a circuit
during the time that the tripping contact remains closed. If the current in the
tripping circuit is maintained over 500 mA, the function is sealed independently of
the status of the function that caused the trip.
Standard output points 32
User output points 32