GEK-106310AB F650 Digital Bay Controller A-1
APPENDIX A A.1 LOGIC OPERANDS
A
APPENDIX A LOGIC OPERANDSA.1LOGIC OPERANDS
OPERANDS - F650 - MODEL FX - GX
INTERNAL SYSTEM STATUS
AUTOCHECK INTERNAL STATES (CRITICAL)
DSP Internal States (Critical to metering and
protection)
DSP COMM ERROR
DSP Communication Error: (0) Rignt communications
between DSP and main processor; (1) Communication
Error between DSP and main processor
MAGNETIC MODULE
ERROR
Magnetic Module Error: (0) Right Communication
between DSP and magnetic module processor; (1)
Communication Error between DSP and magnetic
module processor
CALIBRATION ERROR
Calibration Error: (0) Right calibration values stored; (1)
The calibration values stored are out of the calibration
limits.
Flash Internal States (Critical to Relay configuration
and stored data)
E2PROM STATUS
E2prom status :(0) Not configured or problems during
writing process ; (1) Configured and OK
IO Board States (Critical to operation and
protection)
BOARD F STATUS
Board F status: (0) Inactive - There is no communication
with the board (1) Active - There is communication with
the board.
BOARD G STATUS
Board G status: (0) Inactive - There is no communication
with the board (1) Active - There is communication with
the board.
BOARD H STATUS
Board H status: (0) Inactive - There is no communication
with the board (1) Active - There is communication with
the board.
BOARD J STATUS
Board J status: (0) Inactive - There is no communication
with the board (1) Active - There is communication with
the board.
IEC61850 INTERNAL STATES (NON CRITICAL)
IEC61850 Internal States ICD STATUS
UNKNOWN: when the relay has not the IEC61850 proto-
col in the relay model the ICD status is unknow to the
unit
ICD ERROR: There is an error in the ICD file and the
relay ICD is not operative. To solve this issue it is neces-
sary to send a correct ICD to the relay using the
IEC61850 configurator tool. When the ICD error is raised
the IEC 61850 will not be operative (the IEC 61850 cli-
ent, reports and gooses will not work). It is advisable to
include the ICD ERROR in the main error signal config-
ured by the customers in their applications.
MODIFIED: The settings have been changed in the icd
but they are still not wrtten in the icd file in the relay
IN PROGRESS: The icd setting are being written to the
file in the relay
OK WITHOUT DAIS: The relay has not got the "Use DOI
&DAI" setting enabled (true) and it is working properly
with the ICD file.
OK: The relay has got the "Use DOI &DAI" setting
enabled (true) and it is working properly with the ICD file.
When that setting is set to true the icd setting will prevail
over the relay settings.
OTHER INTERNAL STATES (NON CRITICAL)

Table of Contents

Other manuals for GE F650

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F650 and is the answer not in the manual?

GE F650 Specifications

General IconGeneral
BrandGE
ModelF650
CategoryController
LanguageEnglish

Related product manuals