11-4 F650 Digital Bay Controller GEK-106310AB
11.1 EXAMPLE 1: COMMUNICATION & PROTECTION SETTINGS PROCEDURE 11 APPLICATION EXAMPLES
11
Under
SETPOINT  RELAY CONFIGURATION  LEDS
Under
SETPOINT  RELAY CONFIGURATION  OPERATIONS
Select Operation 0
Command Text Reset C Output 00
Interlock Type None
Interlocks ---
Final State Type None
Final States ---
Frontal Key F1
Contact Input None
Virtual Output None
Time Out 500 (default)
MMI ---
Com1 ---
Com 2 ---
ETH-Master 1 ---
ETH Master 2 ---
ETH Master 3 ---
ETH Master 4 ---
Under
SETPOINT  RELAY CONFIGURATION  OSCILLOGRAPHY
11.1.4 TEST
Apply 7.5 A in phase A (terminals B1-B2) until contact 00 on Board F operates (terminals F19-F21 should be and remain
closed), and LED 5 should be lit. Check that operating time is in the order of 1.7 seconds.
Remove current from terminals B1-B2
Press pushbutton F1 and check that contact 00 on Board F has been open.
Check that LED 5 in the front of the relay has been turned off.
Repeat the process for phase B (terminals B3-B4) and for phase C (terminals B5-B6)
Under Actual  Waveform Capture menu retrieve the last oscillography recording stored, open it using GE_OSC program
and check that the two digital signals as well as the current signal were kept.
SELECT NAME SOURCE
Led 5 C Output Op 00 C Output_00_00
SELECT NAME SOURCE
Digital Channel 1 C Output Op_00_00 C Output Oper_00_00
Digital Channel 2 C Output_00_00 C Output_00_00