100
© 2024 KEB America, Inc.
• During the idle state the input must be active. If not, a brake switch failure error will
be triggered.
• During the start of the run, the input must become inactive within the time period set
by LT01 + LT03 + 500mSec. If not, a brake switch failure error will be triggered.
• During the run, the brake switch input should be inactive. If during the run the input
becomes active, the run is allowed to be completed. In this case, upon switch off of
the STO inputs, a brake switch failure error will be triggered.
Motor Type
Setting Options
NUM
Range
Units
Default
Pass
Level
Ind.
PM
Min.
Max.
Imp.
Met.
RW
RW
Brake Switch 1
-
0
15
-
-
0
Basic
Function Off
0
-
-
-
-
-
-
BRK SW 1 Active
1
Brake Switch 2
-
Function Off
0
BRK SW 2 Active
2
Reset Mode
-
General reset
0
3 Auto resets
4
Forced reset
8
Table 14. LI20 Brake function settings
Setting
Description
Bit
NUM
Function off
Neither brake switch inputs are active
0,1
0
Brake switch
Input 1 Active
The brake switch input X1C.5 is functionally active
0
1
Brake Switch
input 2 active
The brake switch input X1C.6 is functionally active
1
2
General reset
Brake switch faults will automatically reset up to the number
of times adjusted in LX01.
2,3
0
3 Auto resets
The brake switch fault will only reset 3 times, regardless of
the LX01 setting.
2
4
Forced reset
A manual reset of the fault on the drive is required. Even
after a power cycle, no auto reset is possible. Parameter
CH00 Forced Fault Reset will change to a value of îšµ3îš¶. It must
be manually reset to a value of îšµ0îš¶.
3
8
Default = General reset (0)
LI50 UPS Mode
This parameter is only active when an input (LI04-LI11) is set to use the UPS function.
The drive determines which direction will use less power based on brief torque
measurements made before the run and then commands the motor to run in the easy
direction.
Motor Type
Range
Units
Default
Pass
Level
Ind.
PM
Min.
Max.
Imp.
Met.
RW
RW
0
1
-
-
0
Basic
• In default mode (0), with the UPS input active, both directions must be signaled to
activate the function.